Learning goals
- Explain the generation-to-user transformer sequence.
- Connect current to resistive heating losses.
- Compare two transmission voltages at the same sending power.
Follow the system
A generatorA device transferring mechanical energy to electrical energy by electromagnetic induction. supplies electrical energyA conserved quantity transferred between stores by working, heating, electrical processes or radiation, measured in joules.. A step-up transformerA transformer with more secondary than primary turns that increases alternating voltage. raises the alternating potential differenceThe energy transferred per unit charge between two points, measured in volts. before long-distance transmission. step-down transformerA transformer with fewer secondary than primary turns that reduces alternating voltage. then reduce it through distribution stages to suitable voltages for users.
Actual networks have many substations and voltage levels. The diagram follows a generation–transmission–user route, with voltage stepped up before transmission and down before use.
Why raise the voltage?
For the simplified powerThe energy transferred or work done per unit time, measured in watts. model, P = VI. If sending power is fixed, multiplying potential differenceThe energy transferred per unit charge between two points, measured in volts. by ten divides electric currentThe amount of electric charge passing a point per unit time, measured in amperes. by ten. The transformerA device using electromagnetic induction between coils to change alternating voltage. changes voltage and current together rather than creating extra power.
Cables have resistanceThe ratio of potential difference across a component to the current through it, measured in ohms.. Heating loss is I²R, so reducing current by ten reduces that loss by a factor of one hundred for the same cable resistance. The advantage follows from current, not from high voltage being inherently loss-free.
Worked transmission comparison
Compare the same 100 kW sending powerThe energy transferred or work done per unit time, measured in watts. through cables with total resistanceThe ratio of potential difference across a component to the current through it, measured in ohms. 2.0 Ω. At 1.0 kV, I = 100 000/1000 = 100 A and cable heating is 100² × 2.0 = 20 000 W = 20 kW.
At 10 kV, I = 100 000/10 000 = 10 A and cable heating is 10² × 2.0 = 200 W = 0.20 kW. The power reaching the far end is 80 kW or 99.8 kW in this resistive model, before any other losses.
The corresponding line drops are IR = 200 V and 20 V. Receiving-end potential differenceThe energy transferred per unit charge between two points, measured in volts. therefore differs from sending voltage. The example compares sending power, not two loads receiving identical power.
Limits and the final step-down
High potential differenceThe energy transferred per unit charge between two points, measured in volts. requires suitable insulation, clearance and protection; equipment cannot simply operate at arbitrarily high voltage. Real alternating-current networks also involve factors beyond this simple resistive calculation.
Near users, voltage is stepped down to the level required by distribution and appliances. A lower voltage is not automatically safe to touch; the diagram explains energyA conserved quantity transferred between stores by working, heating, electrical processes or radiation, measured in joules. transmission,.
Equations
- P = VI; I = P/V.
- Cable heating power = I²R; line voltage drop = IR. Use consistent SI units.
Common misconceptions
- A step-up transformer does not increase power ideally.
- At fixed transmitted power, voltage and current change in opposite directions.
- Cable loss depends on current squared, not just current.
- Distinguish sending power from receiving power after losses.
Compare transformer voltage and current ratios
Change turns and input readings, then reconcile voltage change with conserved power.
What you see
- Labelled diagrams and numerical outputs describe the same selected state.
How to use it
- Change one control at a time, predict the outcome, then compare the readouts. All controls have keyboard-accessible sliders and step buttons.
- Reset restores every model control to its initial value. Nothing is saved.
What it shows
- Vp/Vs=Np/Ns. For an ideal transformer, VpIp=VsIs. A larger secondary/primary turns ratio gives higher secondary voltage; at fixed power, output current falls. This supports lower-current transmission for a given power. Continuous transformation needs a changing magnetic field, so this model assumes a.c., not steady d.c.
Limits of the model
- An ideal 100%-efficient transformer operates with an alternating supply. Readings use the textbook ideal-transformer voltage/current and power relationships; waveform shape and internal losses are not modelled.
- The selected input power is maintained by adjusting the output load as needed. Changing turns at fixed input power does not keep load resistance fixed. Use the numerical turn labels; the drawn coils are not to scale.
Controls
At these settings, the turns ratio is 2. Each side’s voltage×current gives the same power before rounding. This ideal comparison does not calculate transmission-line losses or real transformer efficiency.
Predict, change and explain
At 6 V primary, 100 primary turns, 200 secondary turns and 12 W input, predict both currents and output voltage. Double secondary turns at the same input power. Explain why higher output voltage does not create extra power, and connect this to transmission at lower current.
Connect the outcome to the Physics
Vp/Vs=Np/Ns. For an ideal transformer, VpIp=VsIs. A larger secondary/primary turns ratio gives higher secondary voltage; at fixed power, output current falls. This supports lower-current transmission for a given power. Continuous transformation needs a changing magnetic field, so this model assumes a.c., not steady d.c.